Author Topic: RRC-1216H Green Heron  (Read 15586 times)

w1ajt

  • Newbie
  • *
  • Posts: 29
    • View Profile
    • Email
RRC-1216H Green Heron
« on: 2015-05-24, 15:07:04 »
I am trying to get the RRC-1216H working with my RT-21 controller.  I think it needs a standard RS-232 cable (works via computer and Com 1 on my RRC-1258) and not a null modem cable which is how I am configured.  However, when I "power on" via the web interface the message is "Rotor not initialized" and "Live Update" is active.  I have tried both my new 1216H and the one I use for my ACOM 2000 with the same results.

Any ideas?

Thanks,
Art - W1AJT

Jan (Microbit)

  • Software Developer
  • Administrator
  • Hero Member
  • *****
  • Posts: 1832
    • View Profile
    • Email
Re: RRC-1216H Green Heron
« Reply #1 on: 2015-05-25, 09:04:44 »
I assume that you have had a look at:

http://www.remoterig.com/downloads/RC1216H-Users_manual.pdf

for a description about the RS-232 connector?

"Rotor not initialized"  means that the RC-1216H is unable to communicate with the RT-21 controller. Could be as you are saying a cable problem for ex.
Always include type of hard/software and version when asking for support.

w1ajt

  • Newbie
  • *
  • Posts: 29
    • View Profile
    • Email
Re: RRC-1216H Green Heron
« Reply #2 on: 2015-05-25, 18:08:43 »
Hi Jan,

Yes, of course I read the manual.  As I said, the same cable was used to interface to Com 1 of my radio 1258 and that works so the cable is good.  The RT-21 communicates at 4800 baud. How is that accomplished with the 1216H given that there is no way to set the serial settings?  Do you have any other suggestions?

Thanks,
Art

Jan (Microbit)

  • Software Developer
  • Administrator
  • Hero Member
  • *****
  • Posts: 1832
    • View Profile
    • Email
Re: RRC-1216H Green Heron
« Reply #3 on: 2015-05-25, 21:51:14 »
Hi Jan,

Yes, of course I read the manual.  As I said, the same cable was used to interface to Com 1 of my radio 1258 and that works so the cable is good.  The RT-21 communicates at 4800 baud. How is that accomplished with the 1216H given that there is no way to set the serial settings?  Do you have any other suggestions?

Thanks,
Art
I asked because it happens people do not do the obvious  ;)

The baud rate is simply fixed in the RC-1216H.

No other suggestions right now that I can think of.
Always include type of hard/software and version when asking for support.

w1ajt

  • Newbie
  • *
  • Posts: 29
    • View Profile
    • Email
Re: RRC-1216H Green Heron
« Reply #4 on: 2015-05-28, 14:48:46 »
Hi Jan,

If there are no suggestions, and the 1216H does not work then I will have to return the 1216H.  I do have my first 1216H working with my ACOM 2000 perfectly after I replaced the defective RS-232 processor as received from Microbit.  I will try to get the second one working with the RT-21 again this weekend.

Thanks,
Art - W1AJT / VE3UTT

Jan (Microbit)

  • Software Developer
  • Administrator
  • Hero Member
  • *****
  • Posts: 1832
    • View Profile
    • Email
Re: RRC-1216H Green Heron
« Reply #5 on: 2015-05-28, 15:06:30 »
That is a good idea! If the 2nd one works with the RT-21 then there is something to compare with and you will know that RS-232 converter/cables are ok.

It would also be possible to connect the RC-1216H's RS232 port to a PCs RS232's port(with a 3 wire cable, rx, tx and ground) and start a serial terminal program at 4800 baud, 8 data bits, 1 stop bit. When clicking on "Power/On" there should appear repetitive "AI2;" printouts. That would at least tell that serial data is getting out of the RC-1216H.
Always include type of hard/software and version when asking for support.

w1ajt

  • Newbie
  • *
  • Posts: 29
    • View Profile
    • Email
Re: RRC-1216H Green Heron
« Reply #6 on: 2015-05-28, 17:19:33 »
Hi Jan,

Yes, I already tried the one working great on my ACOM 2000 and it didn't work on the RT-21 either so I think the new 1216H is probably good.  I will try the new one on the ACOM 2000 and see if that works just to be sure.

I can hook up a terminal program but was already going the test with an RS-232 scanner sitting between the 1216H and the RT-21 next week.  I don't give up easily  :) 

Thanks and I will let you know.

Art

Jan (Microbit)

  • Software Developer
  • Administrator
  • Hero Member
  • *****
  • Posts: 1832
    • View Profile
    • Email
Re: RRC-1216H Green Heron
« Reply #7 on: 2015-05-29, 08:14:52 »
I don't give up easily  :) 
I thought you were about to return it  ;)
Always include type of hard/software and version when asking for support.

w1ajt

  • Newbie
  • *
  • Posts: 29
    • View Profile
    • Email
Re: RRC-1216H Green Heron
« Reply #8 on: 2015-06-05, 15:47:54 »
Hello Jan,

Amazing, three brand new RS-232 cables out of the box were bad from 2 different manufacturers.  Used one of my old RS-232 cables and all worked immediately.  I trouble shot the problem with the Green Heron utility program first.

Thanks for your help and patience.  No wonder you couldn't figure out the problem :-)

I am now fully remote K3/ACOM 2000A/RT-21 - GREAT!

73,
Art - W1AJT/VE3UTT

Jan (Microbit)

  • Software Developer
  • Administrator
  • Hero Member
  • *****
  • Posts: 1832
    • View Profile
    • Email
Re: RRC-1216H Green Heron
« Reply #9 on: 2015-06-08, 08:27:52 »
Thanks for letting us know the RC-1216H was not to blame!  ;)
Always include type of hard/software and version when asking for support.