Webswitch 1216H Support in English => Configuration, Webswitch 1216H => Topic started by: HB9EKK on 2012-10-05, 18:14:55

Title: Monoflop functionality for 1216H
Post by: HB9EKK on 2012-10-05, 18:14:55
Does 1216H provide for a monoflop function? Means, that I can activate a button just for 1 second to steer a microswitch?
Title: Re: Monoflop functionality for 1216H
Post by: Jan (Microbit) on 2012-10-05, 19:34:51
Not from the web pages, but you could achieve something like that using a pulse command, see page:

http://www.webswitch.se/wp/?page_id=342 (http://www.webswitch.se/wp/?page_id=342)
Title: Re: Monoflop functionality for 1216H
Post by: Remote_Mike on 2013-01-30, 21:14:41
Unfortunately the 1216H doesn't support real monoflop functionality. Forget about the HTML commands for this function. Use a real monoflop as NE555 or similar and switch on/off a relay for triggering the NE555.
I am using a K3 and this TRX needs a kind of impulse for startup.

Title: Re: Monoflop functionality for 1216H
Post by: Jan (Microbit) on 2013-01-30, 21:28:47
Unfortunately the 1216H doesn't support real monoflop functionality. Forget about the HTML commands for this function. Use a real monoflop as NE555 or similar and switch on/off a relay for triggering the NE555.
I am using a K3 and this TRX needs a kind of impulse for startup.
How do you define a "real monoflop functionality"?
Title: Re: Monoflop functionality for 1216H
Post by: sm2o on 2013-01-30, 21:59:55
It's not needed for triggering the pwr to K3. You can have it on for ever, just switch it off before you send the "pwr off" command via the serial port

/mike
Title: Re: Monoflop functionality for 1216H
Post by: Remote_Mike on 2013-01-31, 13:26:25
A real monoflop doesn't bouncing like a mechanical relay does.
And if the relays are switched on/off (in terms of monoflop function) the output signal is bouncing because of the mechanical contacts.
The K3 can be switched off by sending a "power off" -command via serial port. But the K3 cannot be switched on via serial port. The K3 needs a small pull down at pin 8 (ACC connector) for remote switching on. This pull down signal must not last for ever it is just a small pull down signal of several milliseconds.
For that reason I trigger a monoflop (NE555) via the relays and the monoflop turns on the K3 remotely (electrically isolated via optocoupler). For K3 power off I am using the power off command via serial port.

Mike
Title: Re: Monoflop functionality for 1216H
Post by: Jan (Microbit) on 2013-01-31, 13:59:17
A real monoflop doesn't bouncing like a mechanical relay does.
And if the relays are switched on/off (in terms of monoflop function) the output signal is bouncing because of the mechanical contacts.
The K3 can be switched off by sending a "power off" -command via serial port. But the K3 cannot be switched on via serial port. The K3 needs a small pull down at pin 8 (ACC connector) for remote switching on. This pull down signal must not last for ever it is just a small pull down signal of several milliseconds.
For that reason I trigger a monoflop (NE555) via the relays and the monoflop turns on the K3 remotely (electrically isolated via optocoupler). For K3 power off I am using the power off command via serial port.

Mike
OK, yes in that context I understand what you mean. Though I think a relay could also have a monoflop function if the thing it controls does not mind that the signal jumps up/down before settle down. It is all about how fast the controlled thing is able to detect changes in the signal.