Author Topic: web switch 10 relais and temperature sensors  (Read 8196 times)

ik4ade

  • Jr. Member
  • **
  • Posts: 32
    • View Profile
    • Email
web switch 10 relais and temperature sensors
« on: 2014-05-17, 10:22:22 »
Is possible to have 10 relays by two 1216H web switches (main and slave) and 2 temperature sensors?
Temperature sensors are connected in BUS A and in BUS B. The internal temperature sensor is connected in BUS A (connections 9 and 10) where there are the connections between 1216H main and 1216H slave. Is ok this parallele connection?
TNX, 73 Franco IK4ADE

Jan (Microbit)

  • Software Developer
  • Administrator
  • Hero Member
  • *****
  • Posts: 1832
    • View Profile
    • Email
Re: web switch 10 relais and temperature sensors
« Reply #1 on: 2014-05-17, 21:12:51 »
When using 1-wire BUS A to connect 2 Webswitches in a master/slave connection in order to get 10 relays in the master BUS A cannot be used for other 1-wire devices like temperature sensors. But connecting multiple temperature sensors on BUS B is supported and so one can have more than one temperature sensor per Webswitch by using BUS B.

Always include type of hard/software and version when asking for support.

ik4ade

  • Jr. Member
  • **
  • Posts: 32
    • View Profile
    • Email
Re: web switch 10 relais and temperature sensors
« Reply #2 on: 2014-05-19, 07:50:25 »
Thank you Jan, 73
Franco